English Deutsch Français Italiano Español Português 繁體中文 Bahasa Indonesia Tiếng Việt ภาษาไทย
All categories

6 answers

The amperage ratings are per phase. Most generators are rated in kW or kVA. For example a 250 kVA generator rated at 480 V 3Ø could handle the following:

250 kVA ÷ 0.48 kV ÷ √3 = 300 amps.

This means each phase can handle 300 amperes.

2007-12-30 11:35:36 · answer #1 · answered by Thomas C 6 · 4 1

Although 3 phase, the amperage on the name plate of genset is always for each phase, meaning the full load ampere that the generator can handle per phase...theres no such thing as total when you speak of 3 phase. Three phase has 3 wires that transmit power (current) so the rating is always based on the full load current per wire (per phase) that the genset can give with out over loading.

There are also rating that indicate as total 3 phase like:

Power in KVA or KW

2007-12-30 19:07:42 · answer #2 · answered by Synchronizers 3 · 3 1

The name plate of a generator normally is for its line current. For a wye connected generator, line current = phase current while in a delta connected unit, the phase current= Line current/1.732

2007-12-30 20:26:25 · answer #3 · answered by Anonymous · 2 0

Current is always for each phase. kW, kVA, Hp are total ratings for the motor.

2007-12-30 22:04:40 · answer #4 · answered by Johnny D 4 · 1 0

kw is kilowatts. the out put of your generator .a load calculation on what you want to run,should be done,then size the generator to accomodate.+ 25% extra should do the job.

2007-12-31 02:32:39 · answer #5 · answered by DAVO 3 · 0 0

It's for the whole shooten' match. Capacities are never rated per phase because it's irrelevant.

2007-12-30 19:06:40 · answer #6 · answered by Johneye 4 · 1 4

fedest.com, questions and answers