It is more stable and immune to noise than, say, a 0-5V output.
By having the low end be something other than 0mA or 0V, the common-mode noise rejection range of the receiving circuit is improved.
2007-04-05 06:24:44
·
answer #1
·
answered by knowmeansknow 4
·
1⤊
0⤋
I don't know why 4-20mA is the standard for current loop analog data, but it's been that way for a long time. The is the best way to transmit analog signals from one place to another in an electrically noisey environment, like a factory. High impedance inputs and voltage signals are far to unreliable over a long wire run.
2007-04-05 06:23:02
·
answer #2
·
answered by Diogenes 7
·
0⤊
0⤋
in addition to answers 2 and 3, there is also 2-10mA standard.
in same cases 0-10mA or 0-20mA can be used. for example in a lab application, where a open loop is not a problem but an increase sensitivity is required.
2007-04-05 08:33:02
·
answer #3
·
answered by bily7001 3
·
0⤊
0⤋
You don't want to go 0 to 20 mA, because at 0, you couldn't tell the difference between an open loop (fault) or a 0 mA signal. Also, for a closed loop, induced noise would show up as a false signal
4 mA is far enough above the noise floor to be a reliably detectable signal.
Anything above 20 mA and power losses start to become a factor and accuracy decreases.
.
2007-04-05 06:23:16
·
answer #4
·
answered by tlbs101 7
·
3⤊