what's the maximum amount of amps that I can load per leg in the secondary 208 volts if the total capacity of the transformer is 75kva= 208 amps ?

2007-01-18 09:55:59 · 2 answers · asked by hector596 2 in Science & Mathematics Engineering

2 answers

Your kva remains same in primary and secondary
Primary current = 75000 / [(sqrt3)(460)] = 94 amps
Secondary current = 75000 / [(sqrt3)(208)] = 208 amps

Your continuous rating is 208 amps >> load 208 amps for continuous operation; but it is a good practice to load 80% capacity = 208 x 0.80 = 166 amps

You can overload the transformer as per IEC standards (IEC 354 and IEC 76) or manufacturer's recommendations

2007-01-18 11:40:13 · answer #1 · answered by Sheen 4 · 0 0

Primery side 94 Ampere and secondery side 208 Amperes

2007-01-18 18:09:45 · answer #2 · answered by Pramod 3 · 0 0