I'm a self empoyed electrician, have been for many years, but have come across a problem that's got me stumped. I've fitted a new split load board into a bar and restaurant. Most of the installation is original, a couple of new rings is all I've put in. Trouble is, whenever something with an inductive load is turned on, like a drill, or a flourescent light fitting, it trips the RCD, even if the fitting is on the non RCD side. The insulation test is reasonable, the worst being around 8 ohms. The RCD tests ok, no trip at half fault. I did think about putting a time delayed RCD on the circuit, but that would take the trip time to around 400 ms, too slow for the regs! Any ideas, anyone..............
2006-11-21
08:16:11
·
11 answers
·
asked by
andygos
3
in
Home & Garden
➔ Maintenance & Repairs
Ok, I didn't solve the actual problem. It Wasnt a neutral fault, as it didn't trip every time something was plugged in or turned on, just if you turned on a big inductive load, like 4 or 5 flourescents at once, or a powerful motor. I got over it by changing the RCD for a regular incomer, and putting RCBOs (individual earth leakage trips) on each of the circuits that required RCD protection.
2006-11-23
08:28:58 ·
update #1