On a high voltage 3-phase "grounded wye" system are ground faults detected by connecting a fault detector from the ground nuetral wire to one of the hot wires? If not, how are faults detected?

2006-11-14 07:11:51 · 4 answers · asked by Anonymous in Science & Mathematics Engineering

4 answers

For three phase AC powered loads, three separate power lines provide power to the load. The voltage waveforms on these three lines differ only in their timing, or phase relationship. A fourth wire may provide a neutral connection to the load. In the case of balanced loads, where the current in each of the three phases is equal, the current in the neutral wire will be zero. The neutral wire may therefore be eliminated, as it is not necessary for the purpose of carrying current. The vector sum of the currents drawn from the three phase lines will be zero with a balanced load. A non-zero sum of the current indicates an unbalanced load and that a current is returning to the generator, or current source, via an unintended path. This is the ground fault current.

The ground fault current for a three-phase system, without neutral, may be measured by performing a vector summation of the phase currents. This summation may be performed by a current sensing transformer with the phase currents passing through the common aperture in parallel. The magnetic field induced in the transformer core is then the vector sum of the three individual phase currents and the voltage induced in the secondary winding placed on the transformer provides a signal representing the vector sum of the currents, the ground fault current.

The electrical characteristics of ground faults in solidly grounded WYE systems allow for simple detection of ground currents by monitoring the phase and neutral currents for a simple unbalance in those currents. The principle is that the current going to the load on the normal phase and neutral conductors should return via those same conductors. Any missing current is deemed a fault to ground on the load side of the detector and, when that unbalance exceeds a set threshold, a ground fault is determined. The basic ways of measuring this unbalance for solidly grounded four-wire systems use one ground sensor surrounding the phase and neutral conductors, four individual current transformers connected in a WYE configuration, or four voltage sources connected in a delta configuration.

2006-11-14 07:29:57 · answer #1 · answered by CanTexan 6 · 0 0

The neutral is designed to carry current from unbalanced three-phase loads. To detect ground faults, you merely sum the current on all conductors (including the neutral). If the currents do not sum to zero, you have a ground fault.

- an electric power engineer

2006-11-14 07:19:40 · answer #2 · answered by Deep Thought 5 · 0 0

As others have suggested if its after the meter then its your situation. if it extremely is the case then you definately should not be messing with it besides as 480V is an commercial or commercial voltage. If it extremely is an commercial plant there ought to be a team of electricians accessible for this job. If it is a commercial corporation and no electricians are accessible you ought to call an electric powered contractor to accomplish this artwork. the actual risk from 480V isn't lots the electrocution risk. There are electrocution hazards with all voltages 50V and better. the vast risk with 480V is arc flash. This voltage is severe adequate to take care of an electric powered arc which will produce great blast energies and warmth. there is lots artwork carried out to objective to maintain arc flash to a low point to avert injury of workers ought to they inadvertently reason an arc. There are 2 parameters that dramatically impression the arc flash potential. The length of time the arc is persevered and the fault modern-day. a number of the a thank you to avert or decrease the incident arc flash energies are to furnish appropriate circuit coordination with an on the spot placing on the breaker. The on the spot placing will trip the breaker quicker, reducing the incident potential. the main easy style of fault is a line to floor fault, the main easy thank you to avert it extremely is to furnish a resistance grounded independent which will decrease the fault modern-day to a low fee (often 5 amps on a 480V equipment). If the independent is resistance grounded and additionally you have a line to floor fault then looking the fault turns into effortless. maximum resistance grounded structures have a thumper which will reason the floor and section modern-day to pulsate. Ammeters can then be used to song out the offending component of cable so as that it is repaired or replaced.

2016-12-14 07:07:58 · answer #3 · answered by ? 4 · 0 0

try here:http://rds.yahoo.com/_ylt=A0geuoVdI1pFk28ANJpXNyoA;_ylu=X3oDMTE2cTlsMmRsBGNvbG8DZQRsA1dTMQRwb3MDOARzZWMDc3IEdnRpZANERlg1XzMw/SIG=15an9anm0/EXP=1163621597/**http%3a//www.geindustrial.com/solutions/engineers/docs/der035.pdf%23search='Power%2520Engineers%253A%2520how%2520are%2520ground%2520faults%2520detected'