What are the advantages and disadvantages each for a delta power system and a grounded Y power system? I am referring this as a high voltage distribution system (2.2kv to 69kv).

2006-07-21 03:37:31 · 4 answers · asked by Anonymous in Science & Mathematics Engineering

4 answers

Wye systems obviously have a convenient point to connect to ground. It is generally not the wye or delta system per se, power systems that have delta primaries on the transformers with wye secondaries do not pass ground fault currents through the transformer. Therefore, a power system that was established in this way has better, more sensitive protection, from ground faults. You only have to co-ordinate your ground fault protection back to the transformer.

You can also limit the ground fault current in a wye system with a resistor in the ground connection.

2006-07-23 15:07:50 · answer #1 · answered by buderosdad1 2 · 0 0

Grounding on a Y system is always at the source of the line so that any ground faults will operate a GF relay and open the breaker. Y grounded systems keep each leg at 120° to each other regardless of out of balance loads.
Delta systems are ungrounded and a short to ground will not necessarily trip the breaker. Unbalanced loads will cause a vector shift which can cause overheating in TXFMRS and motors and failures.

2006-07-21 08:05:39 · answer #2 · answered by Barrie66 2 · 0 0

Sounds like an interested question

2016-07-27 04:46:27 · answer #3 · answered by ? 3 · 0 0

very good question

2016-08-23 02:22:04 · answer #4 · answered by lily 4 · 0 0