9500W If run on 230V will be 41.3Amp

45Amp 30mA RCBO/45amp MCB with 30mA protection via split load RCD will be needed

You didnt say what meter run it was but im guessing 30m?
My voltdrop calculater says 6mm Twin and earth but I would still go for 10mm:

Clipped Direct or Embedded in NON-thermal Insulation

Required Cable Size 6mm (I would still use 10mm)

Voltage Drop 9volts.

Percentage Drop 3.9%.

Load = 41.3amps.

2007-11-23 23:34:56 · answer #1 · answered by Ashrightuk 3 · 0 0

10mm twin and earth 45amp rcd matey .
Regards Spadger (electrician to the stars)

2007-11-22 21:04:44 · answer #2 · answered by spadger 1 · 1 0

# 8 Copper

2007-11-22 21:11:28 · answer #3 · answered by gotech 4 · 0 1

10mm cable.

2007-11-22 21:03:50 · answer #4 · answered by Mary Beth's Ex 3 · 0 0