Hi I have a combination boiler runs fine on the central heating side but when i use the domestic hot water it starts making a growning sound and will later trip out. After resetting the thermostat reset button it will then run again I installed the system about 10 years ago this its first problem any ideas
what it could be.
2007-11-15
04:22:57
·
6 answers
·
asked by
moc
2
in
Home & Garden
➔ Do It Yourself (DIY)
when the hot water is run the boiler will start making a groaning noise after one and a half minutes. will contine to make the same noise until a total running time of four and half minutes the boiler will trip then requiring to set the overheat thermostat reset button. Thanks for the answers so far
2007-11-17
01:24:43 ·
update #1
The system pressure is ok set at 1.5 bar
2007-11-17
01:30:49 ·
update #2
I have now found the cause of the noise water in the expansion vessel thanks to D Whelan for the Answer Cheers Mike
2007-11-17
02:42:52 ·
update #3