#8 is good up to 50 amps- #6 is for 60
2007-11-02 16:03:02
·
answer #1
·
answered by tb417 2
·
0⤊
1⤋
Assuming it is OK with your local electrical code, 8 would be OK, as it is rated for 50 amps and there is little chance you will be using the 4 burners and the oven at the same time.
Buy if you want peace of mind and are planning to use the 4 burners and oven at the same time, go for the 6.
2007-11-02 09:36:28
·
answer #2
·
answered by oscarloco 2
·
0⤊
1⤋
15 amp = 14 ga.
20 amp = 12 ga.
30 amp = 10 ga.
40 amp = 8 ga.
50 amp = 6 ga.
2007-11-02 10:29:00
·
answer #3
·
answered by rico3151 6
·
1⤊
0⤋
8 AWG wire is suitable for 50 amp circuits. Voltage drop will not be a factor inside of any typical house, and is usually only a factor for very long wire runs (hundreds of feet).
2007-11-02 09:42:21
·
answer #4
·
answered by Anonymous
·
0⤊
1⤋
#8 cooper SER is what you will need this is for a four wire system which the NEC code requires. this will be 2 hots 1 neutral and a ground. Hope this helps. Voltage drop will not affect you at all. GOOD LUCK
2007-11-02 09:52:14
·
answer #5
·
answered by John T 2
·
0⤊
1⤋
Depending on how long the run is going to be.You'll have a voltage drop so figure that in. Measure your run and go to a electrical supply place and they can give you the right wire.
2007-11-02 09:09:49
·
answer #6
·
answered by sllde 3
·
0⤊
1⤋
# 8 is for 40A.
You need #6 minimum if the cable is copper.
It should tell you this in the instructions or
on the nameplate.
2007-11-02 17:45:23
·
answer #7
·
answered by Irv S 7
·
1⤊
0⤋
#6 copper, 4 wire.
Don't take electrical advise from untrained and unqualified people. Nor phony electricians.
2007-11-04 02:05:37
·
answer #8
·
answered by John himself 6
·
0⤊
0⤋
6ga is the correct answer. after the applicable code provisions are applied 8 is only good for 40a circuits.
2007-11-02 14:07:23
·
answer #9
·
answered by Anonymous
·
1⤊