Turn of the breaker and take the working outlet from the wall.
Probably you will see the problem. The working outlet feeds the others. Probably you will either find a burnt connection on the outlet or some lose wire nut connectors.
Although outlets all look the same, they are either rated at 15 or 20 amp capacities. A 20 amp outlet is for use with #12 electrical wire which can handle 20 amps. 20 amp circuits should be used for most type of appliance as you were using. However #12 wire handling 20 amps should not be connected to a 15 amp outlet.. When you had your appliances going 20 amps were too much for the outlet and either burned out the outlet or overheated the connections.
You should replace all the outlets with the appropriate size.
This is a very common problem and unfortunately the overheating can result in a fire. Hope this is a clear explanation.
2007-10-08 04:05:50
·
answer #1
·
answered by jimmiv 4
·
0⤊
0⤋
3 of the plugs will be on a different circuit to the other one.
Look in the breaker box again. There should be a row of switches (NOT the main switch). One of these will be off. Turn it on. If you don't have a modern box, and you have old fashioned fuses, you will have to work out which one has gone and fix it with fuse wire.
If that is not the problem you need an electrician. Good luck
2007-10-08 03:43:44
·
answer #2
·
answered by Copper 4
·
1⤊
0⤋
Check to see if there is an outlet in the bathroom. Some of these are protected against people dropping a hair dryer into the bath. There is a red button on it. If that switch is on the same line as the steamer, it may have popped.
;-D Push the button back in. Use a lower amp device on that line and put the steamer on the other line.
2007-10-08 03:51:26
·
answer #3
·
answered by China Jon 6
·
0⤊
0⤋
If you have already turned the breaker off and on, that is probably not your problem at this point if all the outlets are controlled from the same one.. Verify that none of the other outlets are a GFI type. Ground faults can easily trip and shut power off to several outlets. Older styles have a red and black button on them, newer styles have an indicator light. If this is not the case, then you will need to turn OFF power to the outlet that is working and remove it from the box. No need to unwire, just unscrew it and pull it away so you can make sure no wires have come loose. If all looks good then post again for more possible situations.
2016-05-18 23:21:31
·
answer #4
·
answered by Anonymous
·
0⤊
0⤋
Have you just been switching off the main supply or is it the actual breaker to that part of the electrical circuit. You may find that the Socket that still works is in a different circuit..although it is in the same room it may be a spur taken off the upstairs ring main
2007-10-08 04:33:18
·
answer #5
·
answered by Gary T 2
·
0⤊
0⤋
Most other people say its breakers.
maybe, but it seems you've checked that.
How about you have a loose wire, either the live or neutral loose would give you these symptoms.
however, if this does turn out to be the case that means you have a "radial" circuit rather than a ring main. This is old fashioned and could account for burnt wires if the load is high.
If it does turn out to be a radial circuit you should look to replace this sooner rather than later.
2007-10-08 04:36:46
·
answer #6
·
answered by Michael H 7
·
0⤊
0⤋
it sounds like you may have overloaded the circuit.
Have you checked the fues in the fusebox. There will be a number of cartridges with a wire fuse in them for each circuit in the house, One for the lights upstairs, one down, one for the sockets upstairs, one down plus other cicruits for showers, boilers etc,
The one you need to look for will have a red marking on it.
Check the fuse in one of the red cartridges (TURN THE POWER OFF FIRST THO AT THE MAIN SWITCH)
if it is not a wire type switch, try resetting the button / switch on one of the red fuses.
be careful, and do not do this with wet hands,
If in doubt get in a pro
good luck :)
2007-10-08 03:45:00
·
answer #7
·
answered by Banjo 2
·
0⤊
0⤋
It sounds as though the other three are on a different circuit to the one which is working. Check the fuse box again as this is the most likely place to find the fault.
2007-10-08 03:46:18
·
answer #8
·
answered by focus 6
·
0⤊
0⤋
If one (or more) of the plugs is a GFI outlet, you probably need to reset the GFI breaker (the buttons located on the plug).
2007-10-08 03:37:41
·
answer #9
·
answered by Daniel T 5
·
0⤊
0⤋
check the plugs or outlets if they are blackened or deformed.
I recommend kopez for outlets except the for the one you need to put in an electrical box because they use thermoplastic.
2007-10-08 03:45:50
·
answer #10
·
answered by Rowin 3
·
0⤊
0⤋