The link that I've attached has a table with wire guage and current capacity. It also has a calculator that you can use to determine the correct wire size given current, and distance from breaker box to kitchen. You should use a wire that will meet the limit of the breaker on your fuse panel. That way in the event of a short circuit, the breaker will trip before your wire is overloaded.
2007-08-09 04:41:11
·
answer #2
·
answered by richard Alvarado 4
·
0⤊
0⤋
What is the amperage rating of the stove? If it's:
30 Amps 10/3 AWG
50 Amps 8/3 AWG
60 Amps 6/3 AWG
2007-08-09 06:37:54
·
answer #3
·
answered by Anonymous
·
0⤊
0⤋
. A stove typically draws 32 - 40 amps. You need a minimum #8 AWG copper Eight AWG copper is rated for 50 amps .
I would definitely use the four prong plug which incorporates a ground. If you look on your stove, you will find a nameplate with the voltage and amperage rating. These nameplates are usually either on the inside edge of the oven or the back of the stove.
2007-08-09 06:34:41
·
answer #4
·
answered by petethen2 4
·
1⤊
0⤋
Not surprised for yr concern, however I am not sure I assume you are staying in USA, meantime instead of getting you more concerned, The best and safe way I would strongly suggest, when You purchase the stoves which you prefer, ask the shop, You need a price tag with the stoves and installation this is their obligation, at least we have this system in the far east, rather than get some electrician who may get things more complicated and you may regret, good luck
2016-05-17 22:04:05
·
answer #5
·
answered by rosalind 3
·
0⤊
0⤋
Just want to add to Greg W's advise
Careful making the connections from aluminum wire to outlets and breakers! use ONLY AL/CU rated equipment.
He is right on about the separate ground/neutral being required in the new code. A long overdue correction.
2007-08-12 10:56:20
·
answer #6
·
answered by john the engineer 3
·
0⤊
0⤋
to comply with code
Install a 4 prong 50 Amp Range Plug
wire size # 6/3 With ground
use a 2 pole 50 amp breaker
be-careful taking advice from those claiming to be experienced electricians!
Note to John:
existing units are still able to use the 3 wire system.
All new circuit wiring must comply to current NEC.
I welcome you to the trade but please,before you get someone hurt,buy a new copy of the code book.
2007-08-11 19:27:12
·
answer #7
·
answered by greg w 3
·
0⤊
0⤋
Usually a stove is connected to a 240 volt 50 amp circuit. That would be a double pole 50 amp circuit breaker and number 6 romex wire. 6 - 2 with ground. And a standard range receptacle.
2007-08-09 04:00:15
·
answer #8
·
answered by John himself 6
·
2⤊
2⤋
Up here you would need a double 40 amp breaker and 8/3 wire for a stove. Be carefull!!! There's a lot of juice flowing there!!!!!
2007-08-09 03:06:11
·
answer #9
·
answered by albertaguy7 3
·
0⤊
1⤋
The wattage rating should be on a plate on the appliance. Read the wattage required and ask the shop for the recommended cable and breaker size for the appliance.
2007-08-09 02:58:12
·
answer #10
·
answered by veg_rose 6
·
0⤊
0⤋
The documentation for your new stove will include the rated load in both Watts and amperes, and minimum wire size and receptacle type.
At 35' you don't need to be concerned with voltage drop.
In general:
Load...........Breaker...........Wire (Copper)
Up to 30A......30A...............3 #10 + G.
Up to 40A.......40A..............3 #8 + G.
Up to 60A.......60A..............3 #6 + G.
(A 50 A. may well be spec'd. but #6 wire is still required)
2007-08-09 16:23:56
·
answer #11
·
answered by Irv S 7
·