Does it meet NEC code, from electrical panel to junction box 30 inches away.

2007-05-01 07:39:59 · 6 answers · asked by deeta63 2 in Home & Garden Do It Yourself (DIY)

It is water tight flex conduit. Thanks for all the answers! I've got it done.

2007-05-01 09:24:34 · update #1

6 answers

You can put up to 6 #10 conductors in a 1/2 " PVC conduit. I would use THHN for easier installation and you can get cut pieces in some of the Home centers.

2007-05-01 08:02:58 · answer #1 · answered by norman8012003 4 · 0 0

hi
here is the table chart
Trade Size Wire Size (THWN, THHN) Conductor Size AWG/kcmil 14 12 10 8 6 4 3 2 1 1/0
1/2 EMT 12 9 5 3 2 1 1 1 1 1
IMC 14 10 6 3 2 1 1 1 1 1
GRC 13 9 6 3 2 1 1 1 1 1

2007-05-01 08:37:11 · answer #2 · answered by pcc122 4 · 1 0

The Revelation of Jesus Christ is the perfect fit with the 'Law and Prophets' of Judaism and the 'Testimony'[N.T.] of Christianity. Regarding: 1st last & last 1st 1. The first chapter of the 1st book of the Law has 22 creations so the last book of the last Testament has 22 chapters. 2. Rev1:19 John wrote The Revelation[the last things] first and his Gospel[the first things he saw] last Babylon and the red beast[Rev17] BOTH have VERY specific histories with Israel and Judea and are a sign for coming times (Ecc1:9 & 3:15) as history does repeat itself. There is no understanding of The Revelation without a deep understanding of the Law & Prophets for The Revelation is the fulfillment[in time] of the words spoken in[all] the O.T. Revelation7 calls out 12,000 people of each of 12 tribes of Israel for a total of 144,000 to play big parts in the last days. According to The Revelation the city of Jerusalem will have an earthquake where 1/10 of the city will collapse and 7000 people will die after two prophets testify to the world from that city for 1260 days[3+1/2 years: half a week of years]

2016-03-18 22:04:15 · answer #3 · answered by Anonymous · 0 0

yes its legal but i wouldent sugest it for many reasons. 1 look like crtap. 2 sutch a small size sealtite will be not so mutch fun to jam wires in without damaging.best of luck to ya

2007-05-01 15:50:20 · answer #4 · answered by mike__996 2 · 0 0

It will be a tight fit. If its going to run near capicity, you might have to derate the wire too.

Don't be a Tight AZZ and do the job twice, go 1 inch and be sure and safe.

2007-05-01 07:49:02 · answer #5 · answered by honker 4 · 2 0

Sure it will fit. No problem. Good luck

2007-05-01 07:43:31 · answer #6 · answered by Fordman 7 · 0 0

Yes and Yes.

2007-05-01 07:49:40 · answer #7 · answered by ROBERT C 5 · 0 0