The gas man red-tagged my hot water tank for several reasons. I'm replacing the tank but also need to change the vent from single wall to double wall (Type B Gas Vent). It goes through the block wall in basement and is very tight fit. Single wall is approx. 3" diameter and double wall is about 3.5". It needs to be double wall where it goes through the wall. How can I enlarge the 3" diameter hole to 3.5"? Can't possibly afford to hire someone. Can do water/gas hookups safely myself. Vent from exterior of block wall on up is double wall. Man said single wall vent wouldn't possibly get hot enough to ignite concrete(!) or have condensation problem if hole is TIGHT (it is, that's the problem) but his hands are tied b/c code states double wall vent _through_ the wall even if the wall isn't flammable. I'm at the "panic stage" since they won't approve the new tank I'm going to install w/o the vent fixed. Thanks in advance for help soonest!
2006-11-17
04:52:22
·
6 answers
·
asked by
Wes G
1
in
Home & Garden
➔ Maintenance & Repairs
I guess my real fear was damaging the wall with the BFH & cold chisel method. Or having the block crack in such a fashion that I wouldn't be able to repair it with hydraulic cement.
I do not know if they are the two hole or the three hole variety. The house was built in 1952.
Unless I hear different in the next couple of hours I will go with the BFH & cold chisel route. I don't imagine I would be able to actually make a round hole only 1/2" larger in diameter - that's only 1/4" enlargement all the way around. I guess "it's gonna' get messy."
Thanks to everyone who answered, this site is new to me.