I have a Worcester (BOSCH) Combi boiler and when I top up the system pressure using fill valve the gauge doesn't move straight away but will have gone up to 2bar about 4 hrs later. Shouldn't this be instant ? What could be wrong ? The gauge reads 0 after about 4 weeks and I have to refill again.

2006-11-02 23:09:04 · 3 answers · asked by paulxm29 1 in Home & Garden Do It Yourself (DIY)

3 answers

I am quite sure you have air in the (heating) system.
It would explain the delayed reading of your pressure gauge, because - as you refill - the air just gets compressed, without actually increasing the water pressure.
Try to "bleed" ALL your radiators, and then refill again.

2006-11-03 02:34:15 · answer #1 · answered by Marianna 6 · 0 0

Possible air in the system or faulty gauge.

2006-11-03 01:56:06 · answer #2 · answered by edgarrrw 4 · 0 0

sounds like an air-lock or vacuum block