What size electrical conductors run in parallel do you need to feed a 400 amp service

2006-09-29 03:52:04 · 1 answers · asked by john t 1 in Education & Reference Homework Help

1 answers

There are different sizes depending on how many sets, conduits, etc, plus I won't do your homework for you. But, yes, each wire in a conduit is counted for derating. You don't even say what kind of service, so using 3 phase 3 wire as an example, if you put the whole thing in one conduit and 2 wires per phase would be 6 current carrying wires in a conduit, and would need to be derated. If you split it into 2 conduits, each having 3 (one from each phase), then you wouldn't derate. Because of this I believe multiple conduits are common for parallel installations.

2006-10-02 03:35:51 · answer #1 · answered by An electrical engineer 5 · 0 0