Technically, you don't convert mA into VA in any AC circuit! One is a measure of current flow, the other is a measure of power.
Now if you want to figure out the power of the transformer, simply multiply the amperage by the voltage.
P = 12V X 800mA = 12V X 0.8A = 9.6 VA or 9.6 watts.
Now you can think of the power in terms of VARs (volt amp reactive), but those are typically used in where you have either a(an) inductive and/or capacitive load and use imaginary numbers to solve such problems.
2006-06-25 08:42:40
·
answer #1
·
answered by cat_lover 4
·
1⤊
0⤋
VA = Watts. Your transformer is rated at 0.8 Amps, and giving a potential of 12 volts. Transformers MUST be AC, cannot be DC. Therefore, VA = Watts, 12 X 0.8 = 9.6 watts as rated. Transformers are usually under rated, so I would suspect the transformer will not burn out its windings at upto 12 Watts, certain not if for a short time period. Oh, and mA = milliamps (1/1000 amp).
2006-06-25 05:19:57
·
answer #2
·
answered by Anonymous
·
0⤊
0⤋
Convert Milliamps To Amps
2016-10-21 13:13:45
·
answer #3
·
answered by ? 4
·
0⤊
0⤋
if you assume that all terms are "rms", then it's simple:
VA = 12 * .8 = 0.96
If the stated values are NOT rms, then there's too much "noise" to give an accurate answer.
NOTE that when you hear of "120 vac", it means RMS, since the peak-to-peak value of the stuff coming out of the wall is typically 170 volts or so.
2006-06-25 05:23:46
·
answer #4
·
answered by atheistforthebirthofjesus 6
·
0⤊
0⤋
What is the 12AC ?????????
2006-06-25 05:21:11
·
answer #5
·
answered by ag_iitkgp 7
·
0⤊